Electrician's - Help Needed!!!!

Spot light in my flat has blown and tripped the switch. Took the light fitting down and theres burnt marks on the wiring and the black box has crumpled and looks like its partly melted.

Called the maintenance bloke and he's saying if the electrician comes and its just the bulb that needs changing I'm gonna get the invoice, not the landlord.

Looking at the picture, does it look like more than simply changing the bulb??

Cheers.

image

Comments

  • Options
    WSSWSS
    edited April 2014
    Bit small that pic mate - can't really see what's going on...

    @Glasshalfempty or @buckshee‌ are your men.
  • Options
    WhatsApp minter or oggs
  • Options

    WhatsApp minter or oggs

    oh yeah! cheers.
  • Options
    by the looks of it Gary it's some kind of junction box , probably a loose connection inside has caused some sparking which has melted it a bit.

    What does the lamp holder itself look like inside , can't see from that angle.
  • Options
    edited April 2014
    buckshee said:

    by the looks of it Gary it's some kind of junction box , probably a loose connection inside has caused some sparking which has melted it a bit.

    What does the lamp holder itself look like inside , can't see from that angle.

    cheers mate. its got burn marks on the inside, but no visible damage from what i can remember (currently at work)

    If the sparky comes out, will he have to do a bit of repair work on it?
  • Options
    If the junction box bit is melted he'll just have to replace that , same goes for the lamp holder. Easy job for him really.
  • Options
    buckshee said:

    If the junction box bit is melted he'll just have to replace that , same goes for the lamp holder. Easy job for him really.

    happy days, as long as he has to do work to justify the call out then I'm happy.

    cheers for the info.
  • Options
    By the looks of it and what you say then yes he will have to do something. Be careful though as he may be under instruction from the landlord to make it look like something he didn't need come out for . When he cuts the old junction box off ask him if you can take a couple of decent photos of it just to cover yourself.
  • Options
    edited April 2014
    VG that's the connector block melted, that's been caused by it sitting on top of the lamp which get extremely hot, simple to rectify mate would take all of 2 minutes, lamp holder will not need replacing just the main cable will need to be stripped back a bit as it will be very brittle. I see this all the time a very common fault with downlights.
  • Options
    cheers chaps
  • Sponsored links:


  • Options
    Switch to led lights.
  • Options
    By regs now downlighters are either meant to be he sealed in variety or have to have a fireproof hood to prevent this sort of thing.

    image


    image



    Like smiffyboy says it's likely to have been caused by it sitting on the lamp or as I said by a loose connection in the block.
  • Options
    If you look at the photo where the ceiling cut out is it does look like it has some form of hood up there
  • Options
    smiffyboy said:

    If you look at the photo where the ceiling cut out is it does look like it has some form of hood up there

    May well be right there actually. The trouble with the hood type is that they mean the connection can still touch the top of the lamp. Also speaking on a professional (lazy) level I prefer the sealed ones as they are easy to install.